    Default 3-Phase Help

    Does anyone know if a motor wired for 208 y three phase can be run using 240 delta three phase?

  2. #2
    Join Date
    Oct 2010
    Posts
    38
    Post Thanks / Like
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)

    Default Re: 3-Phase Help

    I always check with these guys:

    Transformers, Phase Converters and VFD

  3. #3
    Join Date
    Aug 2011
    Location
    Beechworth, VIC
    Posts
    2,535
    Post Thanks / Like
    Mentioned
    10 Post(s)
    Tagged
    0 Thread(s)

    Default Re: 3-Phase Help

    Short answer: no, the voltages are wrong.

    Here's an easy way to visualise this: draw an equilateral triangle point up. Draw in the centre point (1/3 of bisector). Connect each vertex to the centre point. The lengths of the sides are the delta voltages, the lengths of the centre arms are the wye voltages. Since the arms are 2/3 of the bisector and the bisector is 2/SQRT3 of the length of the sides, the ratio of the two is SQRT3.

    208 x SQRT3 = 360.

    Longer answer: are you sure about the voltages you quote? Usually 208V is the phase to phase voltage giving 120V phase to neutral. 240V phase to phase is therefore about 20% higher

  4. #4
    Join Date
    Sep 2010
    Posts
    65
    Post Thanks / Like
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)

    Default Re: 3-Phase Help

    Quote Originally Posted by Mark Kelly View Post
    Short answer: no, the voltages are wrong.

    Here's an easy way to visualise this: draw an equilateral triangle point up. Draw in the centre point (1/3 of bisector). Connect each vertex to the centre point. The lengths of the sides are the delta voltages, the lengths of the centre arms are the wye voltages. Since the arms are 2/3 of the bisector and the bisector is 2/SQRT3 of the length of the sides, the ratio of the two is SQRT3.

    208 x SQRT3 = 360.

    Longer answer: are you sure about the voltages you quote? Usually 208V is the phase to phase voltage giving 120V phase to neutral. 240V phase to phase is therefore about 20% higher

    This might be the most informed and best worded reply i have ever read on this site. Bravo sir! Bravo!

  5. #5
    Join Date
    Dec 2009
    Location
    New York, NY, USA
    Posts
    232
    Post Thanks / Like
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)

    Default Re: 3-Phase Help

    Quote Originally Posted by Brownbird View Post
    Does anyone know if a motor wired for 208 y three phase can be run using 240 delta three phase?
    James,
    you could wire up a VFD to convert* the 208(?) wye to 240 delta.

    *(perhaps mimic is a better word)

    I've done some similar set-ups. Feel free to shoot me an email or call if need be.
    Seth Rosko
    Rosko Cycles
    New York City
    www.rosko.cc

  6. #6
    Join Date
    Aug 2011
    Location
    Beechworth, VIC
    Posts
    2,535
    Post Thanks / Like
    Mentioned
    10 Post(s)
    Tagged
    0 Thread(s)

    Default Re: 3-Phase Help

    Quote Originally Posted by suicideking View Post
    This might be the most informed and best worded reply i have ever read on this site. Bravo sir! Bravo!
    Thanks but it's also wrong. I meant to say "Since the arms are 2/3 of the bisector and the bisector is SQRT3/2 of the length of the sides, the ratio of the two is SQRT3".